If I have three identical inverters rated @ 3kwac, and 240VAC, on a residential system, (non-back up), what would be the best utility disconnect rating for this system?

Comments

Hi pathic,

You need to multiply the inverter output current with 1.25 to find the appropriate AC disconnect rating.

I attach the Long Beach, CA permit authority document that tells you how to calculate what you are looking for. It's also explained in NEC code book.

File Attachment(s)

Hi Bas,

Thanks for the explanation. Can you please tell the book or source from which you picked the above image.

Thanks in advance.

Ammar.

Submitted
13 years 7 months ago
Asked by
Missing Missing