What is the NetID coded switch on the Piggy-Back set to for the Sunny Beam vs Sunny Explorer on a PC ?

Comments

The documentation is somewhat unclear.  If you are using the Sunny Beam, the switch has to be set to '2".  If you are using a PC with Sunny Explorer and a USB Bluetooth device connected on the PC, leave the switch set to  "1" (the default as it comes from the factory).

Footnote: If you are using Sunny Explorer, you do not need the Sunny Beam device as long as you are only monitoring one inverter.