I am looking for a 7000 watt inverter with 2 independent mpp inputs. SMA makes one, but I cannot seem to find it.
Also, I could use a run down on the differences between the SB7000, the SB7000TL, the SB7000TL-US, and the SB7000TL-US-12. The TL, IO know means transformer less, but how does this affect performance? What are the US and 12 for?
Submitted
9 years 11 months ago
Comments
Great questions!
The US designation on these models simply means they are designated for use in the United States. The -10, -12, -22 are model designators that indicate feature charactaristics of each model. For example; the -10 is standard with isolation transformer, the -12 is the same with the addition of AFCI (Arc Fault Current Interupter) and the -22 is the transformerless version with the addition of a secure power supply.
In closing, if you're looking for an SMA inverter in that kW size with dual MPPT channels look no further than the 7 kW. This unit comes with dual MPPT channels, is transformerless and has a secure power supply that will give you 1,500 Watts of backup power on a dedicated circuit when the grid goes down. Something not often seen with batteryless grid-tied inverters.